Across a disconnected initiating circuit pair, the meter reads close to 0 ohm. What is the most likely problem?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2034
- C: A short between the conductors
Explanation
Near zero resistance where the EOL value should be means the conductors touch somewhere, bypassing the EOL. On a conventional zone a short usually shows up as an alarm or a trouble, depending on the panel.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2035A panel shows a ground fault. Which technique is commonly used to locate it on a long circuit?
- 2036What sound level meter weighting is used to measure fire alarm audibility?
- 2037At what height above the floor are audibility measurements normally taken?
- 2038The average ambient sound level in a store is 62 dBA. What minimum fire alarm sound level is needed for public mode, if no louder short-term noise is present?
- 2039In a factory, the average ambient is 70 dBA but a machine produces 88 dBA for several minutes at a time. What minimum public mode sound level is needed?
- 2040In a private mode signaling area, such as a nurses station, how far above the average ambient must the signal be?