Question 2039 of 299 · NICET Fire Alarm Systems Level I
In a factory, the average ambient is 70 dBA but a machine produces 88 dBA for several minutes at a time. What minimum public mode sound level is needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2039
- B: 93 dBA
Explanation
Compare the two options: 70 + 15 = 85 dBA, and 88 + 5 = 93 dBA for a sound lasting 60 seconds or more. The greater value, 93 dBA, applies.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2040In a private mode signaling area, such as a nurses station, how far above the average ambient must the signal be?
- 2041In sleeping areas, what minimum sound level is required at the pillow, besides the 15 dB over ambient rule?
- 2042Which audible signal frequency is required for alarm signals that awaken sleeping occupants in sleeping areas where required by NFPA 72?
- 2043What is the maximum sound pressure level allowed for audible fire alarm signals?
- 2044Two horns each produce 80 dBA at a measuring point. What is the combined level at that point?
- 2045A horn measures 90 dBA at 10 ft in a free field. What level would you expect at 20 ft?