Question 2038 of 299 · NICET Fire Alarm Systems Level I
The average ambient sound level in a store is 62 dBA. What minimum fire alarm sound level is needed for public mode, if no louder short-term noise is present?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2038
- C: 77 dBA
Explanation
Public mode signals must be at least 15 dB above the average ambient level, or 5 dB above the maximum sound lasting 60 seconds, whichever is greater: 62 + 15 = 77 dBA.