Question 2054 of 299 · NICET Fire Alarm Systems Level I
To test the transfer to secondary power, the technician switches off the AC branch circuit. What should happen?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2054
- D: The system keeps working on batteries and shows an AC power trouble
Explanation
Loss of primary power must transfer the system to the secondary supply without losing signals, and the panel must show a trouble for the AC loss. Restore AC after the test and confirm the trouble clears.
More questions: Maintenance (Periodic Testing, Repair and Replacement)