Question 2057 of 299 · NICET Fire Alarm Systems Level I
A sprinkler control valve has been closed. What type of signal should the panel show?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2057
- A: Supervisory signal
Explanation
A closed sprinkler valve is an off-normal condition of a fire protection system and is reported as a supervisory signal. A trouble signal is about faults in the fire alarm system itself.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2058During an inspection you see the panel's trouble LED lit and the buzzer was silenced last week. What should you do?
- 2059How often is a visual inspection of control equipment required on a system that is monitored for alarm, supervisory and trouble signals by a supervising station?
- 2060During a visual inspection of smoke detectors, what are you mainly looking for?
- 2061You find a smoke detector that was painted over during a renovation. What is the correct action?
- 2062A new office wall was built and now a smoke detector sits less than a foot from it, inside a small closet created by the wall. What should the technician do?
- 2063A smoke detector head needs to be replaced. Which replacement is acceptable?