Question 2059 of 299 · NICET Fire Alarm Systems Level I
How often is a visual inspection of control equipment required on a system that is monitored for alarm, supervisory and trouble signals by a supervising station?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2059
- C: Annually
Explanation
For monitored systems, the visual inspection of control unit items like fuses, lamps, LEDs and primary power is annual. Unmonitored systems are inspected much more often (weekly).
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2060During a visual inspection of smoke detectors, what are you mainly looking for?
- 2061You find a smoke detector that was painted over during a renovation. What is the correct action?
- 2062A new office wall was built and now a smoke detector sits less than a foot from it, inside a small closet created by the wall. What should the technician do?
- 2063A smoke detector head needs to be replaced. Which replacement is acceptable?
- 2064You replace an addressable smoke detector. What must you make sure of before leaving?
- 2065A 15 cd strobe in a room designed for 30 cd has failed. What should it be replaced with?