Question 2062 of 299 · NICET Fire Alarm Systems Level I
A new office wall was built and now a smoke detector sits less than a foot from it, inside a small closet created by the wall. What should the technician do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2062
- B: Report it, because the change may require adding or relocating devices
Explanation
Building changes can leave areas unprotected or devices in the wrong place. A technician reports the condition to the supervisor and owner so a designer can decide what is needed.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2063A smoke detector head needs to be replaced. Which replacement is acceptable?
- 2064You replace an addressable smoke detector. What must you make sure of before leaving?
- 2065A 15 cd strobe in a room designed for 30 cd has failed. What should it be replaced with?
- 2066A technician finds that a previous service person removed a detector and twisted the wires together to clear a trouble. What should be done?
- 2067A smoke detector reports a maintenance (dirty) alert at the panel. What should be done?
- 2068What is the purpose of drift compensation in a smoke detector?