A 15 cd strobe in a room designed for 30 cd has failed. What should it be replaced with?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2065
- A: A strobe set to the candela rating required by the design
Explanation
Replacement appliances must match the design requirements, so the room gets enough light. Here the record drawings show 30 cd. If the existing device was wrong, the replacement corrects it.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2066A technician finds that a previous service person removed a detector and twisted the wires together to clear a trouble. What should be done?
- 2067A smoke detector reports a maintenance (dirty) alert at the panel. What should be done?
- 2068What is the purpose of drift compensation in a smoke detector?
- 2069An area of a building is having repeated smoke detector nuisance alarms after construction work. What is a likely cause?
- 2070How is a rate-of-rise heat detector correctly tested?
- 2071When testing a duct smoke detector, what else must be checked besides the alarm response to smoke?