Question 2067 of 299 · NICET Fire Alarm Systems Level I
A smoke detector reports a maintenance (dirty) alert at the panel. What should be done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2067
- B: Clean or replace the detector per the manufacturer and confirm it is in range
Explanation
A dirty alert means drift compensation is near its limit. Cleaning or replacing the detector restores it to its listed range before it causes nuisance alarms or fails.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2068What is the purpose of drift compensation in a smoke detector?
- 2069An area of a building is having repeated smoke detector nuisance alarms after construction work. What is a likely cause?
- 2070How is a rate-of-rise heat detector correctly tested?
- 2071When testing a duct smoke detector, what else must be checked besides the alarm response to smoke?
- 2072What should happen when a duct smoke detector that controls air movement goes into alarm during a test?
- 2073How is a manual fire alarm box normally tested?