Question 2076 of 299 · NICET Fire Alarm Systems Level I
A sound level meter used for fire alarm audibility tests should meet which instrument class?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2076
- C: ANSI S1.4 Type 2 or better
Explanation
Measurements are made with a sound level meter meeting ANSI S1.4 Type 2 requirements. ANSI Z87.1 is for eye protection and UL 268 is the smoke detector standard.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2077Which tool is used to deliver test aerosol to a ceiling smoke detector from the floor?
- 2078Before testing, a technician puts some zones in test or disable mode. What must be done at the end of the job?
- 2079The panel and its outputs will be tested, but the owner does not want the sprinkler pump or door holders to operate. What is the right approach?
- 2080How often must a digital alarm communicator transmitter (DACT) send an automatic test signal to the supervising station?
- 2081Which maintenance task applies to vented lead-acid batteries but not to sealed VRLA batteries?
- 2082When battery terminals show white or green corrosion, what should the technician do?