Question 2075 of 299 · NICET Fire Alarm Systems Level I
Sound level measurements of notification appliances are required by NFPA 72 mainly at which tests?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2075
- B: At initial acceptance and reacceptance testing
Explanation
Sound pressure levels are measured at acceptance and reacceptance (after changes that could affect audibility). Routine annual tests verify operation.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2076A sound level meter used for fire alarm audibility tests should meet which instrument class?
- 2077Which tool is used to deliver test aerosol to a ceiling smoke detector from the floor?
- 2078Before testing, a technician puts some zones in test or disable mode. What must be done at the end of the job?
- 2079The panel and its outputs will be tested, but the owner does not want the sprinkler pump or door holders to operate. What is the right approach?
- 2080How often must a digital alarm communicator transmitter (DACT) send an automatic test signal to the supervising station?
- 2081Which maintenance task applies to vented lead-acid batteries but not to sealed VRLA batteries?