Question 2093 of 299 · NICET Fire Alarm Systems Level I
A smoke detector is marked with a listed sensitivity range of 1.0 to 3.5 percent per foot obscuration. The test reads 3.9 percent per foot. What does this mean?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2093
- A: It is outside its range and must be cleaned, recalibrated or replaced
Explanation
A higher percent per foot value means more smoke is needed to alarm, so 3.9 percent is less sensitive than the range allows. Out of range detectors are cleaned, recalibrated or replaced.