Question 2092 of 299 · NICET Fire Alarm Systems Level I
Within what time must a battery charger be able to recharge fully discharged fire alarm batteries?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2092
- B: 48 hours
Explanation
Battery charging equipment must be able to recharge the batteries within 48 hours after a single discharge cycle. After a long power outage, the system must be ready again within two days.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2093A smoke detector is marked with a listed sensitivity range of 1.0 to 3.5 percent per foot obscuration. The test reads 3.9 percent per foot. What does this mean?
- 2094An addressable panel prints sensitivity readings for every smoke detector. May this be used for the required sensitivity test?
- 2095What qualification does NFPA 72 expect from people who inspect, test and maintain fire alarm systems?
- 2096Which statement about a Level I trainee performing tests is true?
- 2097A device fails its annual test and cannot be fixed the same day. What should the technician do?
- 2098What is the difference between a deficiency and an impairment in NFPA 72 terms?