Question 2094 of 299 · NICET Fire Alarm Systems Level I
An addressable panel prints sensitivity readings for every smoke detector. May this be used for the required sensitivity test?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2094
- A: Yes, if the control equipment is listed for that purpose
Explanation
Listed control equipment arranged for the purpose can perform sensitivity testing. The printout serves as the test record and should be kept with the inspection report.