Question 2110 of 299 · NICET Fire Alarm Systems Level I
The ambient sound in a hotel room is 40 dBA. What minimum alarm level is needed at the pillow?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2110
- A: 75 dBA
Explanation
In sleeping areas the level must be the greatest of 15 dB over ambient (55 dBA), 5 dB over the maximum 60 second level, or 75 dBA. Here 75 dBA controls.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2111Which pattern identifies a carbon monoxide alarm signal?
- 2112What should the panel do when a single conventional smoke detector circuit goes into alarm and alarm verification is enabled?
- 2113What does a supervising station do with signals from a protected building?
- 2114After a fire alarm technician finishes a repair to field wiring, what testing is needed?
- 2115Which tool is best for measuring the current drawn by a NAC without opening the circuit?