Question 2107 of 299 · NICET Fire Alarm Systems Level I
During testing, the panel shows an alarm, but the supervising station reports it received a trouble. What does this indicate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2107
- A: The signal transmission or point programming is wrong and must be fixed
Explanation
The supervising station must receive the correct signal type and, where applicable, the correct point. A mismatch can mean wrong programming or wiring of the communicator.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2108A pressure-type waterflow switch is used on a dry pipe sprinkler system. What does it sense?
- 2109On a dry pipe sprinkler system, which condition sends a supervisory signal, not an alarm?
- 2110The ambient sound in a hotel room is 40 dBA. What minimum alarm level is needed at the pillow?
- 2111Which pattern identifies a carbon monoxide alarm signal?
- 2112What should the panel do when a single conventional smoke detector circuit goes into alarm and alarm verification is enabled?
- 2113What does a supervising station do with signals from a protected building?