Question 2113 of 299 · NICET Fire Alarm Systems Level I
What does a supervising station do with signals from a protected building?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2113
- A: It receives them and acts, for example calling the fire department
Explanation
A supervising station monitors alarm, supervisory and trouble signals and takes the required action: dispatching the fire department, calling the owner or notifying service.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2114After a fire alarm technician finishes a repair to field wiring, what testing is needed?
- 2115Which tool is best for measuring the current drawn by a NAC without opening the circuit?
- 2116A NAC carries 1.8 A in alarm and the voltage at the panel is 24 V. The total wire resistance out and back is 2.0 ohm. What voltage reaches the end of the circuit?
- 2117An initiating device circuit has a 3,900 ohm EOL resistor and 24 V across it. What supervisory current flows in normal standby, ignoring the detectors?
- 2118With all appliances operating, the current on a strobe circuit is measured at 2.9 A. The NAC is rated 2.5 A. What should be done?
- 2119What should the technician check when inspecting a remote annunciator?