Question 2129 of 299 · NICET Fire Alarm Systems Level I
How should replacement fuses in a fire alarm panel be chosen?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2129
- D: Same type and rating as marked by the manufacturer
Explanation
Fuses protect the circuit and equipment. A larger rating or bypass removes protection and can damage the panel or cause a fire.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2130What is the normal state of the panel's AC power indicator in standby?
- 2131When inspecting a strobe in a room, the lens is cracked but the strobe still flashes. What should be done?
- 2132Why are batteries disconnected last when powering down a panel for service and connected after AC when powering up, in many manufacturers' instructions?
- 2133A technician must measure the resistance of an initiating circuit. What must be done first?
- 2134Before an insulation resistance (megger) test on field wiring, what must be disconnected?
- 2135After a fire alarm test is finished, which step completes the job on site?