During an annual test, a technician activates a smoke detector, and the panel shows the alarm but no horns sound. Which check comes first?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2128
- A: Whether the notification circuits are silenced or disabled at the panel
Explanation
A common cause is a disabled or silenced NAC left from an earlier step. If the outputs are enabled, check the NAC for opens, shorts or a blown output.