Why are batteries disconnected last when powering down a panel for service and connected after AC when powering up, in many manufacturers' instructions?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2132
- A: Following the sequence protects the panel and prevents false troubles
Explanation
Manufacturers specify a power down and power up order to avoid damaging the power supply and to let the panel start correctly. Always follow the instructions for that panel.