Question 2133 of 299 · NICET Fire Alarm Systems Level I
A technician must measure the resistance of an initiating circuit. What must be done first?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2133
- A: Disconnect the circuit from the panel so it is de-energized
Explanation
Ohmmeters supply their own small current and give false readings or can be damaged on a live circuit. Lift the circuit from the panel terminals before measuring, then reconnect and confirm the trouble clears.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2134Before an insulation resistance (megger) test on field wiring, what must be disconnected?
- 2135After a fire alarm test is finished, which step completes the job on site?
- 2001How often must spot-type smoke detectors receive a functional test?
- 2002When is the first sensitivity test of newly installed smoke detectors required?
- 2003After the first sensitivity test, how often are smoke detector sensitivity tests normally repeated?
- 2004Two consecutive sensitivity tests show a group of smoke detectors stayed within their listed range. What is the maximum interval the tests may then be extended to?