Before an insulation resistance (megger) test on field wiring, what must be disconnected?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2134
- D: All devices, modules and the panel connections on that circuit
Explanation
A megohmmeter applies a high test voltage that can destroy electronic detectors, modules and panel circuits. The conductors are tested with all equipment disconnected.