Question 2004 of 299 · NICET Fire Alarm Systems Level I
Two consecutive sensitivity tests show a group of smoke detectors stayed within their listed range. What is the maximum interval the tests may then be extended to?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2004
- A: 5 years
Explanation
Once the second required test confirms the detectors are within their listed and marked sensitivity range, the interval may be extended to a maximum of 5 years, with records kept of each test.