When fire alarm cables pass through a fire-rated wall, the penetration must be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2073
- D: firestopped to maintain the fire rating
Explanation
Penetrations of fire-resistance-rated walls, floors and ceilings must be firestopped with approved methods so the rating is not reduced.