The minimum conductor size permitted for non-power-limited fire alarm circuits in a multiconductor cable is
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2072
- C: 18 AWG
Explanation
NPLFA circuits may use 18 AWG and 16 AWG conductors, with larger sizes sized for the load. 22 AWG is common in power-limited cable only.