Which equipment marking does NFPA 70 require where a power supply provides PLFA circuits?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1032
- A: Durable, plainly visible marking of each power-limited circuit
Explanation
Fire alarm equipment supplying PLFA circuits must be durably marked where plainly visible to show each circuit that is power-limited. This helps keep PLFA and NPLFA wiring methods correct during installation and service.