Question 1038 of 344 · NICET Fire Alarm Systems Level II
What NFPA 70 requirement applies to fire alarm circuits that are installed behind panels designed to allow access, such as lift-out ceiling tiles?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1038
- D: Cables must not block removal of the panels
Explanation
Access to electrical equipment must not be denied by an accumulation of wires and cables that prevents removal of panels, including suspended ceiling panels.