Question 1033 of 344 · NICET Fire Alarm Systems Level II
A contractor wants to run PLFA cable in an elevator hoistway. What does NFPA 70 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1033
- C: Install it in RMC, IMC, RNC, or EMT raceway
Explanation
In hoistways, PLFA circuit conductors must be installed in rigid metal conduit, rigid nonmetallic conduit, IMC, or EMT, with a limited exception for elevator equipment wiring.
More questions: Installation
- 1034What NEC rule governs fire alarm cable penetrations through fire resistance rated walls?
- 1035Which NFPA 70 article primarily covers fire alarm system wiring?
- 1036PLFA conductors and NPLFA conductors must terminate in the same control unit enclosure. What does NFPA 70 require?
- 1037Which suffix identifies a cable that has been tested to keep circuit integrity during a fire for a specified rating, such as 2 hours?
- 1038What NFPA 70 requirement applies to fire alarm circuits that are installed behind panels designed to allow access, such as lift-out ceiling tiles?
- 1039Before installing devices on a new project, what is the first document a Level II technician should compare against field conditions to build a work plan?