Question 1036 of 344 · NICET Fire Alarm Systems Level II
PLFA conductors and NPLFA conductors must terminate in the same control unit enclosure. What does NFPA 70 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1036
- A: Keep at least 1/4 in. separation or use a barrier
Explanation
Within enclosures, PLFA conductors may be run with power or NPLFA conductors only to connect to the same equipment, with a minimum 6 mm (1/4 in.) separation or a barrier, or the conductors must be routed to keep them separated.
More questions: Installation
- 1037Which suffix identifies a cable that has been tested to keep circuit integrity during a fire for a specified rating, such as 2 hours?
- 1038What NFPA 70 requirement applies to fire alarm circuits that are installed behind panels designed to allow access, such as lift-out ceiling tiles?
- 1039Before installing devices on a new project, what is the first document a Level II technician should compare against field conditions to build a work plan?
- 1040During rough-in, the technician finds that a duct now sits where a smoke detector is shown on the approved drawing. What is the correct action?
- 1041Which item must be installed so that the fire alarm system wiring does not degrade over time and terminations stay reliable?
- 1042What does NFPA 72 require for the primary power source of a fire alarm system?