Question 1036 of 344 · NICET Fire Alarm Systems Level II

PLFA conductors and NPLFA conductors must terminate in the same control unit enclosure. What does NFPA 70 require?

Exactly one answer is correct.

Show solution

Correct answer to question 1036

  • A: Keep at least 1/4 in. separation or use a barrier

Explanation

Within enclosures, PLFA conductors may be run with power or NPLFA conductors only to connect to the same equipment, with a minimum 6 mm (1/4 in.) separation or a barrier, or the conductors must be routed to keep them separated.