Question 1078 of 344 · NICET Fire Alarm Systems Level II
At what height above the floor are audible notification levels measured for compliance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1078
- C: 5 ft
Explanation
Sound pressure levels are measured 5 ft (1.5 m) above the floor in the area required to be served, unless the AHJ or the design specifies otherwise for a particular space.
More questions: Installation
- 1079What audible signal frequency is required to awaken occupants in sleeping areas?
- 1080In sleeping areas, which audible level is required at the pillow?
- 1081What is the maximum sound pressure level a fire alarm audible signal may produce?
- 1082What is the purpose of system commissioning before the acceptance test?
- 1083During an initial acceptance test, which devices must be tested?
- 1084Before connecting field wiring to the control unit, which test checks for unintended grounds and stray voltage on new circuits?