Question 1075 of 344 · NICET Fire Alarm Systems Level II
Where should a wall mounted audible notification appliance be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1075
- C: Top at least 90 in. above floor and 6 in. below ceiling
Explanation
Wall mounted audible appliances are mounted so the entire top is at least 90 in. (2.29 m) above the floor and at least 6 in. (152 mm) below the ceiling, unless combination units with visibles set other limits.
More questions: Installation
- 1076In public mode, an audible signal must exceed the average ambient sound level by at least how much?
- 1077In private mode (for example, a staff only area), an audible signal must exceed the average ambient sound by at least how much?
- 1078At what height above the floor are audible notification levels measured for compliance?
- 1079What audible signal frequency is required to awaken occupants in sleeping areas?
- 1080In sleeping areas, which audible level is required at the pillow?
- 1081What is the maximum sound pressure level a fire alarm audible signal may produce?