In sleeping areas, which audible level is required at the pillow?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1080
- C: The greater of 15 dB above ambient, 5 dB above the 60 s maximum, or 75 dBA
Explanation
In sleeping areas, the signal must reach at least 15 dB above average ambient, 5 dB above the maximum level lasting 60 s, or 75 dBA, whichever is greater, measured at the pillow.