Question 1102 of 344 · NICET Fire Alarm Systems Level II

Where must the relay or control module that operates an emergency control function be located?

Exactly one answer is correct.

Show solution

Correct answer to question 1102

  • C: Within 3 ft of the controlled component

Explanation

The relay or other device that controls an emergency control function must be within 3 ft (1 m) of the controlled circuit or appliance, unless the wiring between them is monitored for integrity or the system is designed fail safe.

Next to question ›