Question 1104 of 344 · NICET Fire Alarm Systems Level II
What must happen to the fire alarm system when an emergency control function interface relay fails?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1104
- B: A fault in the monitored wiring is annunciated as trouble
Explanation
Wiring between the control unit and the emergency control function interface device is monitored for integrity. An open, short, or ground there produces a trouble signal at the control unit.
More questions: Installation
- 1105Which interface must be provided so that elevators are not recalled to a floor where the lobby detector is in alarm?
- 1106What should a technician do before connecting the fire alarm system to the supervising station during installation?
- 1107Which of these devices is used to check that a wireless (low power radio) initiating device will communicate reliably before final installation?
- 1108How long may a low power radio (wireless) initiating device take to report an alarm signal to the control unit?
- 1109A technician installs a heat detector in an attic where temperatures reach 170 F. Which temperature rating classification is most appropriate?
- 1110What minimum difference is required between a fixed temperature heat detector's rating and the maximum expected ambient ceiling temperature?