How are HVAC fan shutdown circuits typically installed when they are not monitored for integrity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1103
- B: With the relay within 3 ft of the fan controller
Explanation
If the wiring from the relay to the controlled equipment is not supervised, the relay must be within 3 ft of the equipment, so a fault in an unmonitored run cannot prevent the shutdown.