How are HVAC fan shutdown circuits typically installed when they are not monitored for integrity?

Exactly one answer is correct.

Show solution

Correct answer to question 1103

  • B: With the relay within 3 ft of the fan controller

Explanation

If the wiring from the relay to the controlled equipment is not supervised, the relay must be within 3 ft of the equipment, so a fault in an unmonitored run cannot prevent the shutdown.