Question 1101 of 344 · NICET Fire Alarm Systems Level II
Which control function is commonly wired from a fire alarm relay to release magnetically held smoke doors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1101
- D: A fail safe relay that removes holder power on alarm
Explanation
Door holders are electromagnets that hold doors open while energized. On alarm, the relay removes power and the doors close. Loss of power or wiring failure also releases the doors, which is fail safe behavior.