A technician installs a heat detector in an attic where temperatures reach 170 F. Which temperature rating classification is most appropriate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1109
- C: Intermediate, rated 175 F to 249 F
Explanation
Heat detectors should be rated at least 20 F above the maximum expected ambient ceiling temperature. With 170 F maximum, a rating of 190 F or more is needed, which falls in the intermediate class (175 F to 249 F). An ordinary detector would risk nuisance alarms.