What minimum difference is required between a fixed temperature heat detector's rating and the maximum expected ambient ceiling temperature?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1110
- A: 20 F
Explanation
The operating temperature of a heat detector must be at least 20 F (11 C) above the maximum expected temperature at the ceiling, to prevent unwanted alarms on hot days.