With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2030
- B: Near 0 ohms
Explanation
With nothing connected at the far end, the two conductors should read open. A reading near 0 ohms means the conductors touch each other, a short circuit.
More questions: Maintenance
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?
- 2032A 24 VDC NAC with a 2.2 kilohm EOL is checked with the panel in normal (supervisory) condition. Which measurement confirms the EOL is in place?
- 2033Why are notification appliances on a supervised NAC polarized (diode blocked)?
- 2034Using Ohm's law, a circuit draws 0.5 A at 24 V. What is the circuit resistance?
- 2035A 24 VDC fire alarm relay coil has a resistance of 1200 ohms. What current does it draw?
- 2036A 24 VDC panel power supply delivers 3 A to its load. How much power is that?