A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2029
- A: A low resistance reading
Explanation
A healthy conductor should show very high insulation resistance to ground. A low reading means the conductor touches ground somewhere, often at a box edge, a nicked jacket, or water in a junction box.
More questions: Maintenance
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?
- 2032A 24 VDC NAC with a 2.2 kilohm EOL is checked with the panel in normal (supervisory) condition. Which measurement confirms the EOL is in place?
- 2033Why are notification appliances on a supervised NAC polarized (diode blocked)?
- 2034Using Ohm's law, a circuit draws 0.5 A at 24 V. What is the circuit resistance?
- 2035A 24 VDC fire alarm relay coil has a resistance of 1200 ohms. What current does it draw?