Question 2081 of 344 · NICET Fire Alarm Systems Level II
A NAC has 12 strobes. The technician removes the EOL resistor and measures resistance across the disconnected field conductors with the meter leads in normal polarity. The reading is a few ohms. What does it indicate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2081
- D: A short between the conductors
Explanation
Polarized appliances block current in the supervisory direction, and with the EOL removed the meter should read open. A few ohms means the conductors touch, often at a pinched wire or a miswired appliance.
More questions: Maintenance
- 2082During an annual test, a horn strobe works on AC power but fails to operate after the panel transfers to batteries. Which is the most likely cause?
- 2083A technician measures 20.8 V at the last appliance in alarm with the panel on batteries. The appliances are listed for 16 V to 33 V. What is the conclusion?
- 2084A strobe NAC draws 2.4 A in alarm. The run is 250 ft one way of 12 AWG solid copper (1.93 ohms per 1000 ft). What is the voltage drop, treating the load at the end?
- 2085An owner asks to add 6 strobes drawing 0.15 A each to an existing NAC that already draws 1.7 A. The NAC is rated 2.5 A. What is the new load?
- 2086A system's measured standby current is 0.45 A and alarm current is 2.8 A. It requires 24 h standby plus 5 min alarm, with the 1.25 aging correction factor applied. What minimum battery capacity is needed?
- 2087An annual test of a 24 V sealed lead acid battery set is done. Which test shows whether the batteries can deliver their rated capacity?