Question 2084 of 344 · NICET Fire Alarm Systems Level II
A strobe NAC draws 2.4 A in alarm. The run is 250 ft one way of 12 AWG solid copper (1.93 ohms per 1000 ft). What is the voltage drop, treating the load at the end?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2084
- C: About 2.3 V
Explanation
Loop length = 2 x 250 = 500 ft, so R = 1.93 x 500 / 1000 = 0.965 ohm. Drop = 2.4 A x 0.965 ohm = 2.32 V. Placing the full load at the end gives a conservative result.
More questions: Maintenance
- 2085An owner asks to add 6 strobes drawing 0.15 A each to an existing NAC that already draws 1.7 A. The NAC is rated 2.5 A. What is the new load?
- 2086A system's measured standby current is 0.45 A and alarm current is 2.8 A. It requires 24 h standby plus 5 min alarm, with the 1.25 aging correction factor applied. What minimum battery capacity is needed?
- 2087An annual test of a 24 V sealed lead acid battery set is done. Which test shows whether the batteries can deliver their rated capacity?
- 2088How often must the battery charger of a fire alarm control unit be tested?
- 2089How are projected beam smoke detectors tested in the field?
- 2090During the annual test of an air sampling smoke detection system, what must be checked from the most remote sampling port?