Question 2086 of 344 · NICET Fire Alarm Systems Level II

A system's measured standby current is 0.45 A and alarm current is 2.8 A. It requires 24 h standby plus 5 min alarm, with the 1.25 aging correction factor applied. What minimum battery capacity is needed?

Exactly one answer is correct.

Show solution

Correct answer to question 2086

  • A: About 13.8 Ah

Explanation

Standby: 0.45 x 24 = 10.8 Ah. Alarm: 2.8 x (5/60) = 0.23 Ah. Sum = 11.03 Ah, times 1.25 = 13.8 Ah. An existing 12 Ah battery set would be too small.

Next to question ›