Question 2089 of 344 · NICET Fire Alarm Systems Level II
How are projected beam smoke detectors tested in the field?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2089
- D: With listed test filters or the manufacturer's method
Explanation
Beam detectors are tested per the manufacturer, usually with calibrated test filters that simulate a set obscuration. Blocking the beam completely usually causes a trouble signal, not an alarm.
More questions: Maintenance
- 2090During the annual test of an air sampling smoke detection system, what must be checked from the most remote sampling port?
- 2091How should a multicriteria detector (for example smoke plus heat) be functionally tested?
- 2092A carbon monoxide detector connected to the fire alarm system signals end of life. What must be done?
- 2093How often must door release, fan shutdown, and other emergency control functions be tested?
- 2094During an annual test, a duct smoke detector alarms but the air handler keeps running. Which item should be checked first?
- 2095An emergency voice/alarm communication system is tested. What must be verified for the speakers in each acoustically distinguishable space?