Question 2091 of 344 · NICET Fire Alarm Systems Level II
How should a multicriteria detector (for example smoke plus heat) be functionally tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2091
- B: Test each sensing input per the manufacturer
Explanation
Each sensor that contributes to the alarm decision must be tested using the manufacturer's method. Testing only one input leaves the others unverified.
More questions: Maintenance
- 2092A carbon monoxide detector connected to the fire alarm system signals end of life. What must be done?
- 2093How often must door release, fan shutdown, and other emergency control functions be tested?
- 2094During an annual test, a duct smoke detector alarms but the air handler keeps running. Which item should be checked first?
- 2095An emergency voice/alarm communication system is tested. What must be verified for the speakers in each acoustically distinguishable space?
- 2096A technician is asked to replace a failed 24 V power supply board with one from a different manufacturer. What applies?
- 2097Smoke from a test aerosol triggers a detector, but the panel shows the alarm about 60 s later than expected. What feature is most likely enabled?