Question 2097 of 344 · NICET Fire Alarm Systems Level II
Smoke from a test aerosol triggers a detector, but the panel shows the alarm about 60 s later than expected. What feature is most likely enabled?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2097
- B: Alarm verification
Explanation
Alarm verification holds the first alarm, resets the detector, and waits for a confirming alarm. This adds time, which is why the setting and its delay must be checked against the limits.
More questions: Maintenance
- 2098A remote annunciator shows a different zone description than the main panel for the same device. What should the technician do?
- 2099When should a fire alarm system service technician tag a device or system as impaired?
- 2100A smoke detector in a dusty warehouse keeps showing a maintenance alert. What is the correct response?
- 2101Ambient noise in a manufacturing room has risen to an average of 82 dBA since acceptance. The system operates in public mode. What minimum alarm level is needed now?
- 2102Two identical horns each produce 78 dBA at a test point when sounded alone. What level should be expected at that point with both sounding?
- 2103A horn measures 88 dBA at 10 ft. Assuming free field loss, what level is expected at 40 ft?