Question 2101 of 344 · NICET Fire Alarm Systems Level II
Ambient noise in a manufacturing room has risen to an average of 82 dBA since acceptance. The system operates in public mode. What minimum alarm level is needed now?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2101
- A: 97 dBA
Explanation
Public mode requires at least 15 dB above the average ambient level: 82 + 15 = 97 dBA. The total must still stay at or below 110 dBA, and if that cannot be met, visible notification may be used instead where permitted.
More questions: Maintenance
- 2102Two identical horns each produce 78 dBA at a test point when sounded alone. What level should be expected at that point with both sounding?
- 2103A horn measures 88 dBA at 10 ft. Assuming free field loss, what level is expected at 40 ft?
- 2104After an inspection, the service company finds deficiencies it cannot fix that day. What must the report include?
- 2105A technician measures 4.2 kilohms across a Class B IDC at the panel with field wiring disconnected. The EOL is 4.7 kilohms. What is the most likely issue?
- 2001How often must the sensitivity of system smoke detectors be checked after the first check?
- 2002When must the first sensitivity check of a newly installed smoke detector be done?