Question 2099 of 344 · NICET Fire Alarm Systems Level II
When should a fire alarm system service technician tag a device or system as impaired?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2099
- C: Whenever it is out of service or cannot perform
Explanation
An impairment exists whenever the system or part of it is out of service. Tagging and notifying the owner makes the condition visible so mitigation and repair can be arranged.
More questions: Maintenance
- 2100A smoke detector in a dusty warehouse keeps showing a maintenance alert. What is the correct response?
- 2101Ambient noise in a manufacturing room has risen to an average of 82 dBA since acceptance. The system operates in public mode. What minimum alarm level is needed now?
- 2102Two identical horns each produce 78 dBA at a test point when sounded alone. What level should be expected at that point with both sounding?
- 2103A horn measures 88 dBA at 10 ft. Assuming free field loss, what level is expected at 40 ft?
- 2104After an inspection, the service company finds deficiencies it cannot fix that day. What must the report include?
- 2105A technician measures 4.2 kilohms across a Class B IDC at the panel with field wiring disconnected. The EOL is 4.7 kilohms. What is the most likely issue?