A technician measures 4.2 kilohms across a Class B IDC at the panel with field wiring disconnected. The EOL is 4.7 kilohms. What is the most likely issue?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2105
- C: A partial short or leakage path on the circuit
Explanation
A healthy circuit reads about the EOL value plus a few ohms of wire. A lower reading means current takes a parallel path, such as moisture, a damaged device, or a second resistor, and the panel may show trouble or false alarms.