Question 3053 of 344 · NICET Fire Alarm Systems Level II

A NAC must deliver 2.5 A at 400 ft one way, and the allowed drop is 3.4 V. Which is the smallest solid copper conductor that works? (12 AWG = 1.93, 10 AWG = 1.21 ohms per 1000 ft)

Exactly one answer is correct.

Show solution

Correct answer to question 3053

  • C: 10 AWG

Explanation

Maximum loop resistance = 3.4 / 2.5 = 1.36 ohms over 800 ft, or 1.70 ohms per 1000 ft. 12 AWG at 1.93 is too high, while 10 AWG at 1.21 meets it.