Question 3053 of 344 · NICET Fire Alarm Systems Level II
A NAC must deliver 2.5 A at 400 ft one way, and the allowed drop is 3.4 V. Which is the smallest solid copper conductor that works? (12 AWG = 1.93, 10 AWG = 1.21 ohms per 1000 ft)
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3053
- C: 10 AWG
Explanation
Maximum loop resistance = 3.4 / 2.5 = 1.36 ohms over 800 ft, or 1.70 ohms per 1000 ft. 12 AWG at 1.93 is too high, while 10 AWG at 1.21 meets it.
More questions: Submittal Preparation and System Layout
- 3054Why does treating the whole NAC load as if it were at the last appliance give a conservative voltage drop result?
- 3055A 25 V speaker circuit serves 32 speakers tapped at 1 W and 8 speakers tapped at 2 W. What total power does the amplifier need to supply?
- 3056Average ambient sound in an office is 60 dBA. A horn produces 90 dBA at 10 ft. In public mode, would a person 80 ft away (free field) meet the required level?
- 3057Why should ambient sound levels be measured during the site survey of an existing building?
- 3058Corridor horns must awaken occupants in hotel rooms behind closed doors. What layout concern applies?
- 3059Which of these items is a required part of the floor plan on fire alarm shop drawings?